The strange thing is that in slave mode or even when the thing crashes, normally it will give the control to the thermostat but the last few crashes it stops reacting and does not give the control to the thermostat resulting in the boiler not receiving any more commands and when the CS was 70 it will stay 70. When it crashes the logs on the otmonitor stop. I also have the otgw hooked up to home assistant. In the past the integration would render all entities unavailable when the otgw crashes but now it just shows all the last values but doesnt update them anymore. So there is also no way for me to detect it and warn myself when it happens. Also shutting down the otgw doesnt show in home assistant its unavailable. It would be nice if this is fixed so that when there is no communication HA shows the device is unresponsive.
One more thing worth mentioning is the fact that in the past when the otgw crashed a red light came up on the board to show it was crashed now the green led stops flashing (the one showing there is normal communication) but no red error led is burning.
When removing power from the otgw and plug it back in fixed all the problems for a few days. Im not sure whats happening but i did log the otgw up to the point it stops responding. maybe someone can have a look?
Im not sure how much of the log is needed. I have a txt file of around 14MB (to big to add here)
Im running on version 5.3 (newer versions did not work in the past. it wouldnt recognize my thermostat and the thermostat would show no connection)
PIC: 16F88
If someone needs more log entries please let me know. there are 172.000 lines in there

Code: Select all
11:10:35.786435 A50014600 Write-Ack Control setpoint (MsgID=1): 70.00
11:10:36.180513 T00390000 Read-Data Max CH water setpoint (MsgID=57): 0.00
11:10:36.327401 B40394600 Read-Ack Max CH water setpoint (MsgID=57): 70.00
11:10:36.715631 T00110000 Read-Data Relative modulation level (MsgID=17): 0.00
11:10:36.822524 BC0110000 Read-Ack Relative modulation level (MsgID=17): 0.00
11:10:37.256803 T00120000 Read-Data CH water pressure (MsgID=18): 0.00
11:10:37.386067 B40120199 Read-Ack CH water pressure (MsgID=18): 1.60
11:10:37.801758 T80640000 Read-Data Remote override function (MsgID=100): 00000000
11:10:37.832459 R007B0000 Read-Data DHW burner operation hours (MsgID=123): 0
11:10:37.959431 BC07B0138 Read-Ack DHW burner operation hours (MsgID=123): 312
11:10:37.986568 A40640000 Read-Ack Remote override function (MsgID=100): 00000000
11:10:38.327917 T80130000 Read-Data DHW flow rate (MsgID=19): 0.00
11:10:38.436390 B40130000 Read-Ack DHW flow rate (MsgID=19): 0.00
11:10:38.865200 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
11:10:39.003099 BC0191C00 Read-Ack Boiler water temperature (MsgID=25): 28.00
11:10:39.408433 T80730000 Read-Data OEM diagnostic code (MsgID=115): 0
11:10:39.561433 BC07300CB Read-Ack OEM diagnostic code (MsgID=115): 203
11:10:39.943681 T801A0000 Read-Data DHW temperature (MsgID=26): 0.00
11:10:40.057618 B401A0000 Read-Ack DHW temperature (MsgID=26): 0.00
11:10:40.478593 T801C0000 Read-Data Return water temperature (MsgID=28): 0.00
11:10:40.623358 B401C1D00 Read-Ack Return water temperature (MsgID=28): 29.00
11:10:40.992297 PR: I=00
11:10:41.163479 T00000300 Read-Data Status (MsgID=0): 00000011 00000000
11:10:41.199533 R80000200 Read-Data Status (MsgID=0): 00000010 00000000
11:10:41.264554 B40000200 Read-Ack Status (MsgID=0): 00000010 00000000
11:10:41.274934 AC0000300 Read-Ack Status (MsgID=0): 00000011 00000000
11:10:41.706848 T90014600 Write-Data Control setpoint (MsgID=1): 70.00
11:10:41.717431 R10012400 Write-Data Control setpoint (MsgID=1): 36.00
11:10:41.822443 BD0012400 Write-Ack Control setpoint (MsgID=1): 36.00
11:10:41.839799 A50014600 Write-Ack Control setpoint (MsgID=1): 70.00
11:10:42.237697 T80020000 Read-Data Master configuration (MsgID=2): 00000000 0
11:10:42.251222 R00740000 Read-Data Burner starts (MsgID=116): 0
11:10:42.385799 B4074ED4A Read-Ack Burner starts (MsgID=116): 60746
11:10:42.395379 A40020000 Read-Ack Master configuration (MsgID=2): 00000000 0
11:10:42.769059 T00110000 Read-Data Relative modulation level (MsgID=17): 0.00
11:10:42.864750 BC0110000 Read-Ack Relative modulation level (MsgID=17): 0.00
11:10:43.300518 T00120000 Read-Data CH water pressure (MsgID=18): 0.00
11:10:43.431938 B40120199 Read-Ack CH water pressure (MsgID=18): 1.60
11:10:43.838812 T00030000 Read-Data Slave configuration (MsgID=3): 00000000 0
11:10:43.995755 B40034183 Read-Ack Slave configuration (MsgID=3): 01000001 131
11:10:44.376099 T80130000 Read-Data DHW flow rate (MsgID=19): 0.00
11:10:44.482843 B40130000 Read-Ack DHW flow rate (MsgID=19): 0.00
11:10:44.912170 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
11:10:45.050265 BC0191C00 Read-Ack Boiler water temperature (MsgID=25): 28.00
11:10:45.449447 T00060000 Read-Data Remote parameter flags (MsgID=6): 00000000 00000000
11:10:45.607950 B40060301 Read-Ack Remote parameter flags (MsgID=6): 00000011 00000001
11:10:45.986951 T801A0000 Read-Data DHW temperature (MsgID=26): 0.00
11:10:46.099716 B401A0000 Read-Ack DHW temperature (MsgID=26): 0.00
11:10:46.530252 T801C0000 Read-Data Return water temperature (MsgID=28): 0.00
11:10:46.668714 B401C1D00 Read-Ack Return water temperature (MsgID=28): 29.00
11:10:47.217238 T00000300 Read-Data Status (MsgID=0): 00000011 00000000
11:10:47.231398 R80000200 Read-Data Status (MsgID=0): 00000010 00000000
11:10:47.307171 B40000200 Read-Ack Status (MsgID=0): 00000010 00000000
11:10:47.317033 AC0000300 Read-Ack Status (MsgID=0): 00000011 00000000
11:10:47.750594 T90014600 Write-Data Control setpoint (MsgID=1): 70.00
11:10:47.770808 R10012400 Write-Data Control setpoint (MsgID=1): 36.00
11:10:47.872295 BD0012400 Write-Ack Control setpoint (MsgID=1): 36.00
11:10:47.882683 A50014600 Write-Ack Control setpoint (MsgID=1): 70.00
11:10:48.285351 T00090000 Read-Data Remote override room setpoint (MsgID=9): 0.00
11:10:48.324395 R00770000 Read-Data DHW burner starts (MsgID=119): 0
11:10:48.436330 BC0776A74 Read-Ack DHW burner starts (MsgID=119): 27252
11:10:48.446774 AC0090000 Read-Ack Remote override room setpoint (MsgID=9): 0.00
11:10:48.811523 T00110000 Read-Data Relative modulation level (MsgID=17): 0.00
11:10:48.909962 BC0110000 Read-Ack Relative modulation level (MsgID=17): 0.00
11:10:49.352410 T00120000 Read-Data CH water pressure (MsgID=18): 0.00
11:10:49.481753 B40120199 Read-Ack CH water pressure (MsgID=18): 1.60
11:10:49.887381 T00300000 Read-Data DHW setpoint boundaries (MsgID=48): 0 0
11:10:50.041144 BC0303C1E Read-Ack DHW setpoint boundaries (MsgID=48): 60 30
11:10:50.423449 T80130000 Read-Data DHW flow rate (MsgID=19): 0.00
11:10:50.529227 B40130000 Read-Ack DHW flow rate (MsgID=19): 0.00
11:10:50.960750 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
11:10:51.016218 PR: I=00
11:10:51.091270 BC0191C00 Read-Ack Boiler water temperature (MsgID=25): 28.00
11:10:51.498291 T80310000 Read-Data Max CH setpoint boundaries (MsgID=49): 0 0
11:10:51.653787 B40315500 Read-Ack Max CH setpoint boundaries (MsgID=49): 85 0
11:10:52.040826 T801A0000 Read-Data DHW temperature (MsgID=26): 0.00
11:10:52.148452 B401A0000 Read-Ack DHW temperature (MsgID=26): 0.00
11:10:52.572703 T801C0000 Read-Data Return water temperature (MsgID=28): 0.00
11:10:52.709385 B401C1D00 Read-Ack Return water temperature (MsgID=28): 29.00
11:10:53.259927 T00000300 Read-Data Status (MsgID=0): 00000011 00000000
11:10:53.273153 R80000200 Read-Data Status (MsgID=0): 00000010 00000000
11:10:53.360124 B40000200 Read-Ack Status (MsgID=0): 00000010 00000000
11:10:53.369693 AC0000300 Read-Ack Status (MsgID=0): 00000011 00000000
11:10:53.803822 T90014600 Write-Data Control setpoint (MsgID=1): 70.00
11:10:53.816480 R10012400 Write-Data Control setpoint (MsgID=1): 36.00
11:10:53.918131 BD0012400 Write-Ack Control setpoint (MsgID=1): 36.00
11:10:53.936136 A50014600 Write-Ack Control setpoint (MsgID=1): 70.00
11:10:54.323804 T00740000 Read-Data Burner starts (MsgID=116): 0
11:10:54.466466 B4074ED4A Read-Ack Burner starts (MsgID=116): 60746
11:10:54.861029 T00110000 Read-Data Relative modulation level (MsgID=17): 0.00
11:10:54.961985 BC0110000 Read-Ack Relative modulation level (MsgID=17): 0.00
11:10:55.405705 T00120000 Read-Data CH water pressure (MsgID=18): 0.00
11:10:55.521206 B40120199 Read-Ack CH water pressure (MsgID=18): 1.60
11:10:55.942136 T00770000 Read-Data DHW burner starts (MsgID=119): 0
11:10:56.088083 BC0776A74 Read-Ack DHW burner starts (MsgID=119): 27252
11:10:56.473614 T80130000 Read-Data DHW flow rate (MsgID=19): 0.00
11:10:56.575689 B40130000 Read-Ack DHW flow rate (MsgID=19): 0.00
11:10:57.010479 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
11:10:57.138977 B40191B00 Read-Ack Boiler water temperature (MsgID=25): 27.00
11:10:57.548594 T00780000 Read-Data Burner operation hours (MsgID=120): 0
11:10:57.705009 B40780E4E Read-Ack Burner operation hours (MsgID=120): 3662
11:10:58.085910 T801A0000 Read-Data DHW temperature (MsgID=26): 0.00
11:10:58.193563 B401A0000 Read-Ack DHW temperature (MsgID=26): 0.00
11:10:58.623207 T801C0000 Read-Data Return water temperature (MsgID=28): 0.00
11:10:58.755922 B401C1D00 Read-Ack Return water temperature (MsgID=28): 29.00
11:10:59.307748 T00000300 Read-Data Status (MsgID=0): 00000011 00000000
11:10:59.321644 R80000200 Read-Data Status (MsgID=0): 00000010 00000000
11:10:59.401118 B40000200 Read-Ack Status (MsgID=0): 00000010 00000000
11:10:59.411234 AC0000300 Read-Ack Status (MsgID=0): 00000011 00000000
11:10:59.850980 T90014600 Write-Data Control setpoint (MsgID=1): 70.00
11:10:59.860872 R10012400 Write-Data Control setpoint (MsgID=1): 36.00
11:10:59.961831 BD0012400 Write-Ack Control setpoint (MsgID=1): 36.00
11:10:59.971331 A50014600 Write-Ack Control setpoint (MsgID=1): 70.00
11:11:00.372241 T007B0000 Read-Data DHW burner operation hours (MsgID=123): 0
11:11:00.519596 BC07B0138 Read-Ack DHW burner operation hours (MsgID=123): 312
11:11:00.909554 T00110000 Read-Data Relative modulation level (MsgID=17): 0.00
11:11:01.006208 BC0110000 Read-Ack Relative modulation level (MsgID=17): 0.00
11:11:01.043989 PR: I=00
11:11:01.450971 T00120000 Read-Data CH water pressure (MsgID=18): 0.00
11:11:01.574030 B40120199 Read-Ack CH water pressure (MsgID=18): 1.60
11:11:02.002672 T007D0000 Read-Data OpenTherm version Slave (MsgID=125): 0.00
11:11:02.016197 R00780000 Read-Data Burner operation hours (MsgID=120): 0
11:11:02.142038 B40780E4E Read-Ack Burner operation hours (MsgID=120): 3662
11:11:02.151670 AC07D0300 Read-Ack OpenTherm version Slave (MsgID=125): 3.00
11:11:02.522171 T80130000 Read-Data DHW flow rate (MsgID=19): 0.00
11:11:02.628490 B40130000 Read-Ack DHW flow rate (MsgID=19): 0.00
11:11:03.064823 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
11:11:03.186105 B40191B00 Read-Ack Boiler water temperature (MsgID=25): 27.00
11:11:03.596096 T807F0000 Read-Data Slave product version (MsgID=127): 0 0
11:11:03.642557 CS: 36.00
11:11:03.747872 BC07F0326 Read-Ack Slave product version (MsgID=127): 3 38
11:11:04.132926 T801A0000 Read-Data DHW temperature (MsgID=26): 0.00
11:11:04.239518 B401A0000 Read-Ack DHW temperature (MsgID=26): 0.00
11:11:04.670711 T801C0000 Read-Data Return water temperature (MsgID=28): 0.00
11:11:04.802413 B401C1D00 Read-Ack Return water temperature (MsgID=28): 29.00
11:11:05.361575 T00000300 Read-Data Status (MsgID=0): 00000011 00000000
11:11:05.374460 R80000200 Read-Data Status (MsgID=0): 00000010 00000000
11:11:05.392390 CH: 0
11:11:05.516712 B40000200 Read-Ack Status (MsgID=0): 00000010 00000000
11:11:05.526991 AC0000300 Read-Ack Status (MsgID=0): 00000011 00000000
11:11:05.894530 T90014600 Write-Data Control setpoint (MsgID=1): 70.00
11:11:05.907313 R10012400 Write-Data Control setpoint (MsgID=1): 36.00
11:11:06.010179 BD0012400 Write-Ack Control setpoint (MsgID=1): 36.00
11:11:06.027313 A50014600 Write-Ack Control setpoint (MsgID=1): 70.00
11:11:06.420791 T80800000 Read-Data Message ID 128 (MsgID=128): 0
11:11:06.560637 B40800000 Read-Ack Message ID 128 (MsgID=128): 0
11:11:06.958007 T00110000 Read-Data Relative modulation level (MsgID=17): 0.00
11:11:07.058776 BC0110000 Read-Ack Relative modulation level (MsgID=17): 0.00
11:11:07.495322 T00120000 Read-Data CH water pressure (MsgID=18): 0.00
11:11:07.618230 B40120199 Read-Ack CH water pressure (MsgID=18): 1.60
11:11:08.032378 T00050000 Read-Data Application-specific flags (MsgID=5): 00000000 0
11:11:08.177166 BC0050000 Read-Ack Application-specific flags (MsgID=5): 00000000 0
11:11:08.569945 T80130000 Read-Data DHW flow rate (MsgID=19): 0.00
11:11:08.671264 B40130000 Read-Ack DHW flow rate (MsgID=19): 0.00
11:11:09.107237 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
11:11:09.231971 B40191B00 Read-Ack Boiler water temperature (MsgID=25): 27.00
11:11:09.645565 T100E0000 Write-Data Maximum relative modulation level (MsgID=14): 0.00
11:11:09.794422 BD00E0000 Write-Ack Maximum relative modulation level (MsgID=14): 0.00
11:11:10.188246 T801A0000 Read-Data DHW temperature (MsgID=26): 0.00
11:11:10.286627 B401A0000 Read-Ack DHW temperature (MsgID=26): 0.00
11:11:10.722656 T801C0000 Read-Data Return water temperature (MsgID=28): 0.00
11:11:10.852268 B401C1D00 Read-Ack Return water temperature (MsgID=28): 29.00
11:11:11.064042 PR: I=00
11:11:11.410513 T00000300 Read-Data Status (MsgID=0): 00000011 00000000
11:11:11.423662 R80000200 Read-Data Status (MsgID=0): 00000010 00000000
11:11:11.562647 B40000200 Read-Ack Status (MsgID=0): 00000010 00000000
11:11:11.590760 AC0000300 Read-Ack Status (MsgID=0): 00000011 00000000
11:11:11.942010 T90014600 Write-Data Control setpoint (MsgID=1): 70.00
11:11:11.955694 R10012400 Write-Data Control setpoint (MsgID=1): 36.00
11:11:12.059292 BD0012400 Write-Ack Control setpoint (MsgID=1): 36.00
11:11:12.075780 A50014600 Write-Ack Control setpoint (MsgID=1): 70.00
11:11:12.468356 T000F0000 Read-Data Boiler capacity and modulation limits (MsgID=15): 0 0
11:11:12.608007 BC00F1C19 Read-Ack Boiler capacity and modulation limits (MsgID=15): 28 25
11:11:13.005481 T00110000 Read-Data Relative modulation level (MsgID=17): 0.00
11:11:13.103151 BC0110000 Read-Ack Relative modulation level (MsgID=17): 0.00
11:11:13.545007 T00120000 Read-Data CH water pressure (MsgID=18): 0.00
11:11:13.666892 B40120199 Read-Ack CH water pressure (MsgID=18): 1.60
11:11:14.080098 T90101300 Write-Data Room setpoint (MsgID=16): 19.00
11:11:14.224447 B50101300 Write-Ack Room setpoint (MsgID=16): 19.00
11:11:14.621086 T80130000 Read-Data DHW flow rate (MsgID=19): 0.00
11:11:14.715873 B40130000 Read-Ack DHW flow rate (MsgID=19): 0.00
11:11:15.154713 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
11:11:15.278510 B40191B00 Read-Ack Boiler water temperature (MsgID=25): 27.00
11:11:15.695172 T90181391 Write-Data Room temperature (MsgID=24): 19.57
11:11:15.840736 B50181391 Write-Ack Room temperature (MsgID=24): 19.57
11:11:16.229918 T801A0000 Read-Data DHW temperature (MsgID=26): 0.00
11:11:16.333027 B401A0000 Read-Ack DHW temperature (MsgID=26): 0.00
11:11:16.771397 T801C0000 Read-Data Return water temperature (MsgID=28): 0.00
11:11:16.900922 B401C1D00 Read-Ack Return water temperature (MsgID=28): 29.00
11:11:17.458858 T00000300 Read-Data Status (MsgID=0): 00000011 00000000
11:11:17.471949 R80000200 Read-Data Status (MsgID=0): 00000010 00000000
11:11:17.611125 B40000200 Read-Ack Status (MsgID=0): 00000010 00000000
11:11:17.640900 AC0000300 Read-Ack Status (MsgID=0): 00000011 00000000
11:11:17.992086 T90014600 Write-Data Control setpoint (MsgID=1): 70.00
11:11:18.010544 R10012400 Write-Data Control setpoint (MsgID=1): 36.00
11:11:18.101912 BD0012400 Write-Ack Control setpoint (MsgID=1): 36.00
11:11:18.111903 A50014600 Write-Ack Control setpoint (MsgID=1): 70.00
11:11:18.518596 T001D0000 Read-Data Solar storage temperature (MsgID=29): 0.00
11:11:18.653275 BC01D0000 Read-Ack Solar storage temperature (MsgID=29): 0.00
11:11:19.060609 T00110000 Read-Data Relative modulation level (MsgID=17): 0.00
11:11:19.217019 BC0110000 Read-Ack Relative modulation level (MsgID=17): 0.00
11:11:19.592231 T00120000 Read-Data CH water pressure (MsgID=18): 0.00
11:11:19.708280 B40120199 Read-Ack CH water pressure (MsgID=18): 1.60
11:11:20.134905 T001E0000 Read-Data Solar collector temperature (MsgID=30): 0
11:11:20.270166 BC01E0000 Read-Ack Solar collector temperature (MsgID=30): 0
11:11:20.667918 T80130000 Read-Data DHW flow rate (MsgID=19): 0.00
11:11:20.767696 B40130000 Read-Ack DHW flow rate (MsgID=19): 0.00
11:11:21.094036 PR: I=00
11:11:21.210635 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
11:11:21.324860 BC0191C00 Read-Ack Boiler water temperature (MsgID=25): 28.00
11:11:21.742387 T80383C00 Read-Data DHW setpoint (MsgID=56): 60.00
11:11:21.887138 B40383C00 Read-Ack DHW setpoint (MsgID=56): 60.00
11:11:22.279739 T801A0000 Read-Data DHW temperature (MsgID=26): 0.00
11:11:22.378222 B401A0000 Read-Ack DHW temperature (MsgID=26): 0.00
11:11:22.820371 T801C0000 Read-Data Return water temperature (MsgID=28): 0.00
11:11:22.943512 B401C1D00 Read-Ack Return water temperature (MsgID=28): 29.00
11:11:23.507791 T00000300 Read-Data Status (MsgID=0): 00000011 00000000
11:11:23.520888 R80000200 Read-Data Status (MsgID=0): 00000010 00000000
11:11:23.661297 B40000200 Read-Ack Status (MsgID=0): 00000010 00000000
11:11:23.672967 AC0000300 Read-Ack Status (MsgID=0): 00000011 00000000
11:11:24.040847 T90014600 Write-Data Control setpoint (MsgID=1): 70.00
11:11:24.054738 R10012400 Write-Data Control setpoint (MsgID=1): 36.00
11:11:24.148340 BD0012400 Write-Ack Control setpoint (MsgID=1): 36.00
11:11:24.158907 A50014600 Write-Ack Control setpoint (MsgID=1): 70.00
11:11:24.569804 T00390000 Read-Data Max CH water setpoint (MsgID=57): 0.00
11:11:24.706743 B40394600 Read-Ack Max CH water setpoint (MsgID=57): 70.00
11:11:25.104308 T00110000 Read-Data Relative modulation level (MsgID=17): 0.00
11:11:25.262381 BC0110000 Read-Ack Relative modulation level (MsgID=17): 0.00
11:11:25.641608 T00120000 Read-Data CH water pressure (MsgID=18): 0.00
11:11:25.754333 B40120199 Read-Ack CH water pressure (MsgID=18): 1.60
11:11:26.189611 T80640000 Read-Data Remote override function (MsgID=100): 00000000
11:11:26.202567 R007B0000 Read-Data DHW burner operation hours (MsgID=123): 0
11:11:26.331327 BC07B0138 Read-Ack DHW burner operation hours (MsgID=123): 312
11:11:26.341318 A40640000 Read-Ack Remote override function (MsgID=100): 00000000
11:11:26.719780 T80130000 Read-Data DHW flow rate (MsgID=19): 0.00
11:11:26.809629 B40130000 Read-Ack DHW flow rate (MsgID=19): 0.00
11:11:27.253299 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
11:11:27.375182 BC0191C00 Read-Ack Boiler water temperature (MsgID=25): 28.00
11:11:27.790753 T80730000 Read-Data OEM diagnostic code (MsgID=115): 0
11:11:27.933786 BC07300CB Read-Ack OEM diagnostic code (MsgID=115): 203
11:11:28.327909 T801A0000 Read-Data DHW temperature (MsgID=26): 0.00
11:11:28.426783 B401A0000 Read-Ack DHW temperature (MsgID=26): 0.00
11:11:28.865432 T801C0000 Read-Data Return water temperature (MsgID=28): 0.00
11:11:28.989259 B401C1D00 Read-Ack Return water temperature (MsgID=28): 29.00
11:11:29.554371 T00000300 Read-Data Status (MsgID=0): 00000011 00000000
11:11:29.581804 R80000200 Read-Data Status (MsgID=0): 00000010 00000000
11:11:29.706829 B40000200 Read-Ack Status (MsgID=0): 00000010 00000000
11:11:29.717247 AC0000300 Read-Ack Status (MsgID=0): 00000011 00000000
11:11:30.088830 T90014600 Write-Data Control setpoint (MsgID=1): 70.00
11:11:30.104947 R10012400 Write-Data Control setpoint (MsgID=1): 36.00
11:11:30.195723 BD0012400 Write-Ack Control setpoint (MsgID=1): 36.00
11:11:30.205742 A50014600 Write-Ack Control setpoint (MsgID=1): 70.00
11:11:30.632188 T80020000 Read-Data Master configuration (MsgID=2): 00000000 0
11:11:30.647039 R00740000 Read-Data Burner starts (MsgID=116): 0
11:11:30.761336 B4074ED4A Read-Ack Burner starts (MsgID=116): 60746
11:11:30.779267 A40020000 Read-Ack Master configuration (MsgID=2): 00000000 0
11:11:31.119671 PR: I=00
11:11:31.152695 T00110000 Read-Data Relative modulation level (MsgID=17): 0.00
11:11:31.309786 BC0110000 Read-Ack Relative modulation level (MsgID=17): 0.00
11:11:31.689682 T00120000 Read-Data CH water pressure (MsgID=18): 0.00
11:11:31.806864 B40120199 Read-Ack CH water pressure (MsgID=18): 1.60
11:11:32.226931 T00030000 Read-Data Slave configuration (MsgID=3): 00000000 0
11:11:32.363972 B40034183 Read-Ack Slave configuration (MsgID=3): 01000001 131
11:11:32.773517 T80130000 Read-Data DHW flow rate (MsgID=19): 0.00
11:11:32.926294 B40130000 Read-Ack DHW flow rate (MsgID=19): 0.00
11:11:33.303742 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
11:11:33.425361 BC0191C00 Read-Ack Boiler water temperature (MsgID=25): 28.00
11:11:33.840208 T00060000 Read-Data Remote parameter flags (MsgID=6): 00000000 00000000
11:11:33.981856 B40060301 Read-Ack Remote parameter flags (MsgID=6): 00000011 00000001
11:11:34.377570 T801A0000 Read-Data DHW temperature (MsgID=26): 0.00
11:11:34.473267 B401A0000 Read-Ack DHW temperature (MsgID=26): 0.00
11:11:34.919279 T801C0000 Read-Data Return water temperature (MsgID=28): 0.00
11:11:35.042336 B401C1D00 Read-Ack Return water temperature (MsgID=28): 29.00
11:11:35.600066 T00000300 Read-Data Status (MsgID=0): 00000011 00000000
11:11:35.634844 R80000200 Read-Data Status (MsgID=0): 00000010 00000000
11:11:35.750097 B40000200 Read-Ack Status (MsgID=0): 00000010 00000000
11:11:35.771191 AC0000300 Read-Ack Status (MsgID=0): 00000011 00000000
11:11:36.140233 T90014600 Write-Data Control setpoint (MsgID=1): 70.00
11:11:36.153969 R10012400 Write-Data Control setpoint (MsgID=1): 36.00
11:11:36.246315 BD0012400 Write-Ack Control setpoint (MsgID=1): 36.00
11:11:36.256043 A50014600 Write-Ack Control setpoint (MsgID=1): 70.00
11:11:36.674504 T00090000 Read-Data Remote override room setpoint (MsgID=9): 0.00
11:11:36.686508 R00770000 Read-Data DHW burner starts (MsgID=119): 0
11:11:36.811999 BC0776A74 Read-Ack DHW burner starts (MsgID=119): 27252
11:11:36.822120 AC0090000 Read-Ack Remote override room setpoint (MsgID=9): 0.00
11:11:37.202122 T00110000 Read-Data Relative modulation level (MsgID=17): 0.00
11:11:37.355798 BC0110000 Read-Ack Relative modulation level (MsgID=17): 0.00
11:11:37.738096 T00120000 Read-Data CH water pressure (MsgID=18): 0.00
11:11:37.852944 B40120199 Read-Ack CH water pressure (MsgID=18): 1.60
11:11:38.275730 T00300000 Read-Data DHW setpoint boundaries (MsgID=48): 0 0
11:11:38.416950 BC0303C1E Read-Ack DHW setpoint boundaries (MsgID=48): 60 30
11:11:38.812992 T80130000 Read-Data DHW flow rate (MsgID=19): 0.00
11:11:38.972711 B40130819 Read-Ack DHW flow rate (MsgID=19): 8.10
11:11:39.350324 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
11:11:39.470032 BC0191C00 Read-Ack Boiler water temperature (MsgID=25): 28.00
11:11:39.888607 T80310000 Read-Data Max CH setpoint boundaries (MsgID=49): 0 0
11:11:40.027340 B40315500 Read-Ack Max CH setpoint boundaries (MsgID=49): 85 0
11:11:40.430556 T801A0000 Read-Data DHW temperature (MsgID=26): 0.00
11:11:40.521546 B401A0000 Read-Ack DHW temperature (MsgID=26): 0.00
11:11:40.963985 T801C0000 Read-Data Return water temperature (MsgID=28): 0.00
11:11:41.059901 B401C1B00 Read-Ack Return water temperature (MsgID=28): 27.00