junkers boiler and junkers tr 200 thermosthat with OG ?
pluimpje
Post by pluimpje »
I'm new to domotica and everything around it.
My final goal is to integrate my boiler (a junkers eurostar) within the home automation system (openhab environment)
I stumbled upon the opentherm gateway to manipulate the boiler, but does this work with the combo of boiler (junkers eurostar) and thermosthat (junkers tr 200) ?
regards
Re: junkers boiler and junkers tr 200 thermosthat with OG ?
From a quick search on the internet, I don't get the impression the junkers equipment uses opentherm. It is therefor unfortunately very unlikely that you will be able to use the opentherm gateway.
pluimpje
Post by pluimpje »
I found this document http://www.thermosmart.nl/wp-content/up ... 112013.pdf
that says that junkers boiler do opentherm, but the wiring is the same as the on/off (aan/uit in the table) so I already had my doubts.
Any way of checking this since I have the hardware (boiler) without spending a lot of euros ?
A simple check you can start with, assuming you have access to a multimeter, is to disconnect the thermostat and measure the current when the wires are shorted via the multimeter. For opentherm the current should be between 5 and 9 mA.
If that's OK, measure the voltage on the line with the thermostat connected. It should normally be below 7 Volts, with short bursts to a higher voltage about once a second.
If either of these tests show a different result, you know the boiler and thermostat are not compatible with opentherm.