Domoticz: OTGW: Error 03

This Forum is about the Opentherm gateway (OTG) from Schelte

Moderator: hvxl

Domoticz: OTGW: Error 03

Postby Dylantje » Mon Jul 27, 2015 12:33 pm

Dear all..

I do have a OTG usb, what was working very good for a few weeks

I did Persistent my usb devices.[ because sometime my hardware was gone.. ]
And i did try a other 5v power supply, 2000 what was 500 mah
Now i cannot get the OTG good working..
In domoticz i get strange erros.:
Code: Select all
2015-07-27 13:13:08.842 OTGW: Error 03
2015-07-27 13:13:09.304 (D.M.: CV Opentherm) Temp (CV: Control Setpoint)
2015-07-27 13:13:09.334 (D.M.: CV Opentherm) General/Percentage (CV: Maximum Relative Modulation Level)
2015-07-27 13:13:09.357 (D.M.: CV Opentherm) Thermostat (CV: Kamer Setpoint)
2015-07-27 13:13:09.382 (D.M.: CV Opentherm) General/Percentage (CV: Relative modulation level)
2015-07-27 13:13:09.406 (D.M.: CV Opentherm) Temp (CV: Kamer Temperature)
2015-07-27 13:13:09.431 (D.M.: CV Opentherm) Temp (CV: Boiler Water Temperature)
2015-07-27 13:13:09.455 (D.M.: CV Opentherm) Temp (CV: DHW Temperature)
2015-07-27 13:13:09.480 (D.M.: CV Opentherm) Temp (CV: Buiten [ Terras ])
2015-07-27 13:13:09.504 (D.M.: CV Opentherm) Temp (CV: Return Water Temperature)
2015-07-27 13:13:09.529 (D.M.: CV Opentherm) Thermostat (CV: DHW Setpoint)
2015-07-27 13:13:09.552 (D.M.: CV Opentherm) Thermostat (Max_CH Water Setpoint)
2015-07-27 13:13:09.781 OTGW: Error 03
2015-07-27 13:13:09.841 (D.M.:Zwave) Usage (Z: Garage Actueel)
2015-07-27 13:13:09.869 (D.M.:Zwave) Energy (Z: Garage Totaal)
2015-07-27 13:13:10.721 OTGW: Error 03
2015-07-27 13:13:11.660 OTGW: Error 03
2015-07-27 13:13:12.600 OTGW: Error 03
2015-07-27 13:13:13.540 OTGW: Error 03


Please some one?
What can i do..
When i try my old power supply i got the same error strange.....
Dylantje
Member
Member
 
Posts: 180
Joined: January 2013

Re: Domoticz: OTGW: Error 03

Postby hvxl » Thu Jul 30, 2015 4:50 pm

You didn't indicate if you went through the troubleshooting instructions and what the effect was of the suggestion mentioned there for Error 03 situations.
Schelte
hvxl
Senior Member
Senior Member
 
Posts: 1303
Joined: June 2010

Re: Domoticz: OTGW: Error 03

Postby Dylantje » Thu Jul 30, 2015 8:38 pm

Thanks i did not now there was a site/page like this.....

Don not ask me how.
Only the error is gone..

And i see only this about th error 03:
Code: Select all
If you see nothing, or things like "Error 01" or "Error 03", the reference voltage may be wrong.


Only how can i change this????
Dylantje
Member
Member
 
Posts: 180
Joined: January 2013

Re: Domoticz: OTGW: Error 03

Postby hvxl » Thu Jul 30, 2015 8:45 pm

Read the sentence immediately following the one you quoted: "You can modify it via Options → Settings (F5) or with the VR=X command. where X is a number between 0 and 9."
Schelte
hvxl
Senior Member
Senior Member
 
Posts: 1303
Joined: June 2010

Re: Domoticz: OTGW: Error 03

Postby Dylantje » Thu Jul 30, 2015 8:55 pm

Thanks....
Dylantje
Member
Member
 
Posts: 180
Joined: January 2013

Re: Domoticz: OTGW: Error 03

Postby mfranken » Tue Sep 15, 2015 7:41 pm

I have my setup running for a few days and it's not stable. I see a lot of Error 03, just like mentioned in this topic. I am using domoticz too. Today I saw T and B messages too:

Code: Select all
2015-09-15 20:29:53.953 OTGW: Error 03
2015-09-15 20:29:56.816 OTGW: Error 03
2015-09-15 20:30:01.689 OTGW: Error 03
2015-09-15 20:30:04.512 OTGW: Error 03
2015-09-15 20:30:07.355 OTGW: Error 03
2015-09-15 20:30:09.238 OTGW: Error 03
2015-09-15 20:30:14.132 OTGW: Error 03
2015-09-15 20:30:16.014 OTGW: Error 03
2015-09-15 20:30:17.896 OTGW: Error 03
2015-09-15 20:30:19.796 OTGW: Error 03
2015-09-15 20:30:20.301 (Nefit) Temp (Control Setpoint)
2015-09-15 20:30:20.302 (Nefit) General/Percentage (Maximum Relative Modulation Level)
2015-09-15 20:30:20.303 (Nefit) Thermostat (Room Setpoint)
2015-09-15 20:30:20.304 (Nefit) General/Percentage (Relative modulation level)
2015-09-15 20:30:20.305 (Nefit) Temp (Room Temperature)
2015-09-15 20:30:20.305 (Nefit) Temp (Boiler Water Temperature)
2015-09-15 20:30:20.306 (Nefit) Temp (DHW Temperature)
2015-09-15 20:30:20.307 (Nefit) Temp (Outside Temperature)
2015-09-15 20:30:20.308 (Nefit) Temp (Return Water Temperature)
2015-09-15 20:30:20.309 (Nefit) Thermostat (DHW Setpoint)
2015-09-15 20:30:20.309 (Nefit) Thermostat (Max_CH Water Setpoint)
2015-09-15 20:30:21.678 OTGW: Error 03
2015-09-15 20:30:23.560 OTGW: Error 03
2015-09-15 20:32:10.977 OTGW: T00000300
2015-09-15 20:32:11.940 OTGW: T00000300
2015-09-15 20:32:12.029 OTGW: B40000302
2015-09-15 20:32:12.495 OTGW: T00050000
2015-09-15 20:32:13.436 OTGW: T00050000
2015-09-15 20:32:14.377 OTGW: T00050000
2015-09-15 20:32:15.345 OTGW: T00050000
2015-09-15 20:32:16.297 OTGW: Error 03
2015-09-15 20:32:17.227 OTGW: T00000300
2015-09-15 20:32:18.168 OTGW: T00000300
2015-09-15 20:32:19.121 OTGW: Error 03
2015-09-15 20:32:20.051 OTGW: T00000300
2015-09-15 20:32:20.140 OTGW: BC000030A
2015-09-15 20:32:20.605 OTGW: T00000300
2015-09-15 20:32:21.547 OTGW: T00000300
2015-09-15 20:32:21.636 OTGW: BC000030A
2015-09-15 20:32:22.101 OTGW: T00050000
2015-09-15 20:32:22.190 OTGW: BF0050000
2015-09-15 20:32:22.656 OTGW: T10013C00
2015-09-15 20:32:22.745 OTGW: BD0013C00
2015-09-15 20:32:23.211 OTGW: T10013C00
2015-09-15 20:32:23.300 OTGW: BD0013C00
2015-09-15 20:32:23.766 OTGW: T80190000
2015-09-15 20:32:23.855 OTGW: BC01924B3
2015-09-15 20:32:24.347 OTGW: T00110000
2015-09-15 20:32:24.436 OTGW: B40110F62
2015-09-15 20:32:24.902 OTGW: T801C0000
2015-09-15 20:32:24.991 OTGW: BC01C22B3
2015-09-15 20:32:25.457 OTGW: T801A0000
2015-09-15 20:32:25.546 OTGW: BC01A2C33
2015-09-15 20:32:26.011 OTGW: T00000300
2015-09-15 20:32:26.971 OTGW: T00000300
2015-09-15 20:32:27.060 OTGW: BC000030A
2015-09-15 20:32:27.526 OTGW: T001B0000
2015-09-15 20:32:27.615 OTGW: B601B0000
2015-09-15 20:32:28.080 OTGW: T10013C00
2015-09-15 20:32:29.032 OTGW: Error 03
2015-09-15 20:32:29.962 OTGW: T10013C00
2015-09-15 20:32:30.914 OTGW: Error 03
2015-09-15 20:32:31.845 OTGW: T00000300
2015-09-15 20:32:31.934 OTGW: BC000030A
2015-09-15 20:32:32.400 OTGW: T10013C00
2015-09-15 20:32:33.356 OTGW: Error 03
2015-09-15 20:32:34.287 OTGW: T10013C00
2015-09-15 20:32:35.239 OTGW: Error 03
2015-09-15 20:32:36.169 OTGW: T00000300
2015-09-15 20:32:37.254 OTGW: T00000300
2015-09-15 20:32:37.292 (Nefit) Lighting 2 (CH_enabled)
2015-09-15 20:32:37.295 (Nefit) Lighting 2 (CH_active)
2015-09-15 20:32:37.296 (Nefit) Lighting 2 (FlameOn)
2015-09-15 20:32:37.298 (Nefit) Temp (Control Setpoint)
2015-09-15 20:32:37.299 (Nefit) General/Percentage (Maximum Relative Modulation Level)
2015-09-15 20:32:37.300 (Nefit) Thermostat (Room Setpoint)
2015-09-15 20:32:37.301 (Nefit) General/Percentage (Relative modulation level)
2015-09-15 20:32:37.301 (Nefit) Temp (Room Temperature)
2015-09-15 20:32:37.302 (Nefit) Temp (Boiler Water Temperature)
2015-09-15 20:32:37.303 (Nefit) Temp (DHW Temperature)
2015-09-15 20:32:37.304 (Nefit) Temp (Outside Temperature)
2015-09-15 20:32:37.305 (Nefit) Temp (Return Water Temperature)
2015-09-15 20:32:37.306 (Nefit) Thermostat (DHW Setpoint)
2015-09-15 20:32:37.307 (Nefit) Thermostat (Max_CH Water Setpoint)
2015-09-15 20:32:39.003 OTGW: Error 03
2015-09-15 20:32:42.012 OTGW: Error 03
2015-09-15 20:32:48.241 OTGW: Error 03
2015-09-15 20:32:54.996 OTGW: Error 03
2015-09-15 20:32:56.897 OTGW: Error 03
2015-09-15 20:32:59.904 OTGW: Error 03
2015-09-15 20:33:08.731 OTGW: Error 03
2015-09-15 20:33:10.264 (Nefit) Lighting 2 (FlameOn)
2015-09-15 20:33:10.266 (Nefit) Temp (Control Setpoint)
2015-09-15 20:33:10.267 (Nefit) General/Percentage (Maximum Relative Modulation Level)
2015-09-15 20:33:10.268 (Nefit) Thermostat (Room Setpoint)
2015-09-15 20:33:10.269 (Nefit) General/Percentage (Relative modulation level)
2015-09-15 20:33:10.271 (Nefit) Temp (Room Temperature)
2015-09-15 20:33:10.273 (Nefit) Temp (Boiler Water Temperature)
2015-09-15 20:33:10.274 (Nefit) Temp (DHW Temperature)
2015-09-15 20:33:10.275 (Nefit) Temp (Outside Temperature)
2015-09-15 20:33:10.276 (Nefit) Temp (Return Water Temperature)
2015-09-15 20:33:10.278 (Nefit) Thermostat (DHW Setpoint)
2015-09-15 20:33:10.279 (Nefit) Thermostat (Max_CH Water Setpoint)
2015-09-15 20:33:20.051 OTGW: Error 02
2015-09-15 20:33:22.798 OTGW: Error 03
2015-09-15 20:33:24.681 OTGW: Error 03
2015-09-15 20:33:27.134 OTGW: Error 03
2015-09-15 20:33:29.016 OTGW: Error 03
2015-09-15 20:33:34.055 OTGW: Error 03
2015-09-15 20:33:42.485 (Nefit) Lighting 2 (FlameOn)
2015-09-15 20:33:42.487 (Nefit) Temp (Control Setpoint)
2015-09-15 20:33:42.488 (Nefit) General/Percentage (Maximum Relative Modulation Level)
2015-09-15 20:33:42.488 (Nefit) Thermostat (Room Setpoint)
2015-09-15 20:33:42.489 (Nefit) General/Percentage (Relative modulation level)
2015-09-15 20:33:42.490 (Nefit) General/Pressure (CH Water Pressure)
2015-09-15 20:33:42.491 (Nefit) Temp (Room Temperature)
2015-09-15 20:33:42.492 (Nefit) Temp (Boiler Water Temperature)
2015-09-15 20:33:42.494 (Nefit) Temp (DHW Temperature)
2015-09-15 20:33:42.495 (Nefit) Temp (Outside Temperature)
2015-09-15 20:33:42.496 (Nefit) Temp (Return Water Temperature)
2015-09-15 20:33:42.497 (Nefit) Thermostat (DHW Setpoint)
2015-09-15 20:33:42.498 (Nefit) Thermostat (Max_CH Water Setpoint)
2015-09-15 20:33:44.406 OTGW: Error 02
2015-09-15 20:33:54.299 OTGW: Error 03
2015-09-15 20:33:58.253 OTGW: Error 03


Between Errors most of the time the boiler, OTGW and thermostat are behaving normally. Any idea what causes this and what to do?
mfranken
Starting Member
Starting Member
 
Posts: 17
Joined: September 2015

Re: Domoticz: OTGW: Error 03

Postby mfranken » Tue Sep 15, 2015 7:45 pm

My setup, btw is:
my CV (Nefit TopLine Aquapower HRC 45/CW6 + EMS-OT)
Honeywell Touch modulation (TH8210M1003) thermostat
OpenTherm Gateway USB version bougth prebuilt, running latest firmware
Domoticz latest version on MacMIni

mfranken wrote:I have my setup running for a few days and it's not stable. I see a lot of Error 03, just like mentioned in this topic. I am using domoticz too. Today I saw T and B messages too:

Code: Select all
2015-09-15 20:29:53.953 OTGW: Error 03
2015-09-15 20:29:56.816 OTGW: Error 03
2015-09-15 20:30:01.689 OTGW: Error 03
2015-09-15 20:30:04.512 OTGW: Error 03
2015-09-15 20:30:07.355 OTGW: Error 03
2015-09-15 20:30:09.238 OTGW: Error 03
2015-09-15 20:30:14.132 OTGW: Error 03
2015-09-15 20:30:16.014 OTGW: Error 03
2015-09-15 20:30:17.896 OTGW: Error 03
2015-09-15 20:30:19.796 OTGW: Error 03
2015-09-15 20:30:20.301 (Nefit) Temp (Control Setpoint)
2015-09-15 20:30:20.302 (Nefit) General/Percentage (Maximum Relative Modulation Level)
2015-09-15 20:30:20.303 (Nefit) Thermostat (Room Setpoint)
2015-09-15 20:30:20.304 (Nefit) General/Percentage (Relative modulation level)
2015-09-15 20:30:20.305 (Nefit) Temp (Room Temperature)
2015-09-15 20:30:20.305 (Nefit) Temp (Boiler Water Temperature)
2015-09-15 20:30:20.306 (Nefit) Temp (DHW Temperature)
2015-09-15 20:30:20.307 (Nefit) Temp (Outside Temperature)
2015-09-15 20:30:20.308 (Nefit) Temp (Return Water Temperature)
2015-09-15 20:30:20.309 (Nefit) Thermostat (DHW Setpoint)
2015-09-15 20:30:20.309 (Nefit) Thermostat (Max_CH Water Setpoint)
2015-09-15 20:30:21.678 OTGW: Error 03
2015-09-15 20:30:23.560 OTGW: Error 03
2015-09-15 20:32:10.977 OTGW: T00000300
2015-09-15 20:32:11.940 OTGW: T00000300
2015-09-15 20:32:12.029 OTGW: B40000302
2015-09-15 20:32:12.495 OTGW: T00050000
2015-09-15 20:32:13.436 OTGW: T00050000
2015-09-15 20:32:14.377 OTGW: T00050000
2015-09-15 20:32:15.345 OTGW: T00050000
2015-09-15 20:32:16.297 OTGW: Error 03
2015-09-15 20:32:17.227 OTGW: T00000300
2015-09-15 20:32:18.168 OTGW: T00000300
2015-09-15 20:32:19.121 OTGW: Error 03
2015-09-15 20:32:20.051 OTGW: T00000300
2015-09-15 20:32:20.140 OTGW: BC000030A
2015-09-15 20:32:20.605 OTGW: T00000300
2015-09-15 20:32:21.547 OTGW: T00000300
2015-09-15 20:32:21.636 OTGW: BC000030A
2015-09-15 20:32:22.101 OTGW: T00050000
2015-09-15 20:32:22.190 OTGW: BF0050000
2015-09-15 20:32:22.656 OTGW: T10013C00
2015-09-15 20:32:22.745 OTGW: BD0013C00
2015-09-15 20:32:23.211 OTGW: T10013C00
2015-09-15 20:32:23.300 OTGW: BD0013C00
2015-09-15 20:32:23.766 OTGW: T80190000
2015-09-15 20:32:23.855 OTGW: BC01924B3
2015-09-15 20:32:24.347 OTGW: T00110000
2015-09-15 20:32:24.436 OTGW: B40110F62
2015-09-15 20:32:24.902 OTGW: T801C0000
2015-09-15 20:32:24.991 OTGW: BC01C22B3
2015-09-15 20:32:25.457 OTGW: T801A0000
2015-09-15 20:32:25.546 OTGW: BC01A2C33
2015-09-15 20:32:26.011 OTGW: T00000300
2015-09-15 20:32:26.971 OTGW: T00000300
2015-09-15 20:32:27.060 OTGW: BC000030A
2015-09-15 20:32:27.526 OTGW: T001B0000
2015-09-15 20:32:27.615 OTGW: B601B0000
2015-09-15 20:32:28.080 OTGW: T10013C00
2015-09-15 20:32:29.032 OTGW: Error 03
2015-09-15 20:32:29.962 OTGW: T10013C00
2015-09-15 20:32:30.914 OTGW: Error 03
2015-09-15 20:32:31.845 OTGW: T00000300
2015-09-15 20:32:31.934 OTGW: BC000030A
2015-09-15 20:32:32.400 OTGW: T10013C00
2015-09-15 20:32:33.356 OTGW: Error 03
2015-09-15 20:32:34.287 OTGW: T10013C00
2015-09-15 20:32:35.239 OTGW: Error 03
2015-09-15 20:32:36.169 OTGW: T00000300
2015-09-15 20:32:37.254 OTGW: T00000300
2015-09-15 20:32:37.292 (Nefit) Lighting 2 (CH_enabled)
2015-09-15 20:32:37.295 (Nefit) Lighting 2 (CH_active)
2015-09-15 20:32:37.296 (Nefit) Lighting 2 (FlameOn)
2015-09-15 20:32:37.298 (Nefit) Temp (Control Setpoint)
2015-09-15 20:32:37.299 (Nefit) General/Percentage (Maximum Relative Modulation Level)
2015-09-15 20:32:37.300 (Nefit) Thermostat (Room Setpoint)
2015-09-15 20:32:37.301 (Nefit) General/Percentage (Relative modulation level)
2015-09-15 20:32:37.301 (Nefit) Temp (Room Temperature)
2015-09-15 20:32:37.302 (Nefit) Temp (Boiler Water Temperature)
2015-09-15 20:32:37.303 (Nefit) Temp (DHW Temperature)
2015-09-15 20:32:37.304 (Nefit) Temp (Outside Temperature)
2015-09-15 20:32:37.305 (Nefit) Temp (Return Water Temperature)
2015-09-15 20:32:37.306 (Nefit) Thermostat (DHW Setpoint)
2015-09-15 20:32:37.307 (Nefit) Thermostat (Max_CH Water Setpoint)
2015-09-15 20:32:39.003 OTGW: Error 03
2015-09-15 20:32:42.012 OTGW: Error 03
2015-09-15 20:32:48.241 OTGW: Error 03
2015-09-15 20:32:54.996 OTGW: Error 03
2015-09-15 20:32:56.897 OTGW: Error 03
2015-09-15 20:32:59.904 OTGW: Error 03
2015-09-15 20:33:08.731 OTGW: Error 03
2015-09-15 20:33:10.264 (Nefit) Lighting 2 (FlameOn)
2015-09-15 20:33:10.266 (Nefit) Temp (Control Setpoint)
2015-09-15 20:33:10.267 (Nefit) General/Percentage (Maximum Relative Modulation Level)
2015-09-15 20:33:10.268 (Nefit) Thermostat (Room Setpoint)
2015-09-15 20:33:10.269 (Nefit) General/Percentage (Relative modulation level)
2015-09-15 20:33:10.271 (Nefit) Temp (Room Temperature)
2015-09-15 20:33:10.273 (Nefit) Temp (Boiler Water Temperature)
2015-09-15 20:33:10.274 (Nefit) Temp (DHW Temperature)
2015-09-15 20:33:10.275 (Nefit) Temp (Outside Temperature)
2015-09-15 20:33:10.276 (Nefit) Temp (Return Water Temperature)
2015-09-15 20:33:10.278 (Nefit) Thermostat (DHW Setpoint)
2015-09-15 20:33:10.279 (Nefit) Thermostat (Max_CH Water Setpoint)
2015-09-15 20:33:20.051 OTGW: Error 02
2015-09-15 20:33:22.798 OTGW: Error 03
2015-09-15 20:33:24.681 OTGW: Error 03
2015-09-15 20:33:27.134 OTGW: Error 03
2015-09-15 20:33:29.016 OTGW: Error 03
2015-09-15 20:33:34.055 OTGW: Error 03
2015-09-15 20:33:42.485 (Nefit) Lighting 2 (FlameOn)
2015-09-15 20:33:42.487 (Nefit) Temp (Control Setpoint)
2015-09-15 20:33:42.488 (Nefit) General/Percentage (Maximum Relative Modulation Level)
2015-09-15 20:33:42.488 (Nefit) Thermostat (Room Setpoint)
2015-09-15 20:33:42.489 (Nefit) General/Percentage (Relative modulation level)
2015-09-15 20:33:42.490 (Nefit) General/Pressure (CH Water Pressure)
2015-09-15 20:33:42.491 (Nefit) Temp (Room Temperature)
2015-09-15 20:33:42.492 (Nefit) Temp (Boiler Water Temperature)
2015-09-15 20:33:42.494 (Nefit) Temp (DHW Temperature)
2015-09-15 20:33:42.495 (Nefit) Temp (Outside Temperature)
2015-09-15 20:33:42.496 (Nefit) Temp (Return Water Temperature)
2015-09-15 20:33:42.497 (Nefit) Thermostat (DHW Setpoint)
2015-09-15 20:33:42.498 (Nefit) Thermostat (Max_CH Water Setpoint)
2015-09-15 20:33:44.406 OTGW: Error 02
2015-09-15 20:33:54.299 OTGW: Error 03
2015-09-15 20:33:58.253 OTGW: Error 03


Between Errors most of the time the boiler, OTGW and thermostat are behaving normally. Any idea what causes this and what to do?
mfranken
Starting Member
Starting Member
 
Posts: 17
Joined: September 2015

Re: Domoticz: OTGW: Error 03

Postby mfranken » Tue Sep 15, 2015 8:04 pm

Answering my own question for archaeologists sake: I read the troubleshooting guide and attached the OTGW to the otmonitor, set VR=4 and the Errors are gone (for now)
mfranken
Starting Member
Starting Member
 
Posts: 17
Joined: September 2015

Re: Domoticz: OTGW: Error 03

Postby hvxl » Tue Sep 15, 2015 8:46 pm

That was also the suggestion offered to the previous poster in this topic...

By the way: Is Domoticz hiding information? With the latest firmware the OTGW should report additional information after Error 02, which I don't see in your log.
Schelte
hvxl
Senior Member
Senior Member
 
Posts: 1303
Joined: June 2010

Re: Domoticz: OTGW: Error 03

Postby mfranken » Tue Sep 15, 2015 9:38 pm

Thanks, I will check the domoticz implementation
mfranken
Starting Member
Starting Member
 
Posts: 17
Joined: September 2015


Return to Opentherm Gateway Forum

Who is online

Users browsing this forum: No registered users and 0 guests