Dear all..
I do have a OTG usb, what was working very good for a few weeks
I did Persistent my usb devices.[ because sometime my hardware was gone.. ]
And i did try a other 5v power supply, 2000 what was 500 mah
Now i cannot get the OTG good working..
In domoticz i get strange erros.:
Code: Select all
2015-07-27 13:13:08.842 OTGW: Error 03
2015-07-27 13:13:09.304 (D.M.: CV Opentherm) Temp (CV: Control Setpoint)
2015-07-27 13:13:09.334 (D.M.: CV Opentherm) General/Percentage (CV: Maximum Relative Modulation Level)
2015-07-27 13:13:09.357 (D.M.: CV Opentherm) Thermostat (CV: Kamer Setpoint)
2015-07-27 13:13:09.382 (D.M.: CV Opentherm) General/Percentage (CV: Relative modulation level)
2015-07-27 13:13:09.406 (D.M.: CV Opentherm) Temp (CV: Kamer Temperature)
2015-07-27 13:13:09.431 (D.M.: CV Opentherm) Temp (CV: Boiler Water Temperature)
2015-07-27 13:13:09.455 (D.M.: CV Opentherm) Temp (CV: DHW Temperature)
2015-07-27 13:13:09.480 (D.M.: CV Opentherm) Temp (CV: Buiten [ Terras ])
2015-07-27 13:13:09.504 (D.M.: CV Opentherm) Temp (CV: Return Water Temperature)
2015-07-27 13:13:09.529 (D.M.: CV Opentherm) Thermostat (CV: DHW Setpoint)
2015-07-27 13:13:09.552 (D.M.: CV Opentherm) Thermostat (Max_CH Water Setpoint)
2015-07-27 13:13:09.781 OTGW: Error 03
2015-07-27 13:13:09.841 (D.M.:Zwave) Usage (Z: Garage Actueel)
2015-07-27 13:13:09.869 (D.M.:Zwave) Energy (Z: Garage Totaal)
2015-07-27 13:13:10.721 OTGW: Error 03
2015-07-27 13:13:11.660 OTGW: Error 03
2015-07-27 13:13:12.600 OTGW: Error 03
2015-07-27 13:13:13.540 OTGW: Error 03
Please some one?
What can i do..
When i try my old power supply i got the same error strange.....
hvxl
Senior Member
Posts: 2029 Joined: Sat Jun 05, 2010 11:59 am
Contact:
Post
by hvxl » Thu Jul 30, 2015 5:50 pm
You didn't indicate if you went through the
troubleshooting instructions and what the effect was of the suggestion mentioned there for Error 03 situations.
Schelte
Dylantje
Member
Posts: 180 Joined: Sat Jan 05, 2013 9:46 pm
Post
by Dylantje » Thu Jul 30, 2015 9:38 pm
Thanks i did not now there was a site/page like this.....
Don not ask me how.
Only the error is gone..
And i see only this about th error 03:
Code: Select all
If you see nothing, or things like "Error 01" or "Error 03", the reference voltage may be wrong.
Only how can i change this????
hvxl
Senior Member
Posts: 2029 Joined: Sat Jun 05, 2010 11:59 am
Contact:
Post
by hvxl » Thu Jul 30, 2015 9:45 pm
Read the sentence immediately following the one you quoted: "You can modify it via Options → Settings (F5) or with the VR=X command. where X is a number between 0 and 9."
Schelte
mfranken
Starting Member
Posts: 17 Joined: Mon Sep 07, 2015 10:29 am
Post
by mfranken » Tue Sep 15, 2015 8:41 pm
I have my setup running for a few days and it's not stable. I see a lot of Error 03, just like mentioned in this topic. I am using domoticz too. Today I saw T and B messages too:
Code: Select all
2015-09-15 20:29:53.953 OTGW: Error 03
2015-09-15 20:29:56.816 OTGW: Error 03
2015-09-15 20:30:01.689 OTGW: Error 03
2015-09-15 20:30:04.512 OTGW: Error 03
2015-09-15 20:30:07.355 OTGW: Error 03
2015-09-15 20:30:09.238 OTGW: Error 03
2015-09-15 20:30:14.132 OTGW: Error 03
2015-09-15 20:30:16.014 OTGW: Error 03
2015-09-15 20:30:17.896 OTGW: Error 03
2015-09-15 20:30:19.796 OTGW: Error 03
2015-09-15 20:30:20.301 (Nefit) Temp (Control Setpoint)
2015-09-15 20:30:20.302 (Nefit) General/Percentage (Maximum Relative Modulation Level)
2015-09-15 20:30:20.303 (Nefit) Thermostat (Room Setpoint)
2015-09-15 20:30:20.304 (Nefit) General/Percentage (Relative modulation level)
2015-09-15 20:30:20.305 (Nefit) Temp (Room Temperature)
2015-09-15 20:30:20.305 (Nefit) Temp (Boiler Water Temperature)
2015-09-15 20:30:20.306 (Nefit) Temp (DHW Temperature)
2015-09-15 20:30:20.307 (Nefit) Temp (Outside Temperature)
2015-09-15 20:30:20.308 (Nefit) Temp (Return Water Temperature)
2015-09-15 20:30:20.309 (Nefit) Thermostat (DHW Setpoint)
2015-09-15 20:30:20.309 (Nefit) Thermostat (Max_CH Water Setpoint)
2015-09-15 20:30:21.678 OTGW: Error 03
2015-09-15 20:30:23.560 OTGW: Error 03
2015-09-15 20:32:10.977 OTGW: T00000300
2015-09-15 20:32:11.940 OTGW: T00000300
2015-09-15 20:32:12.029 OTGW: B40000302
2015-09-15 20:32:12.495 OTGW: T00050000
2015-09-15 20:32:13.436 OTGW: T00050000
2015-09-15 20:32:14.377 OTGW: T00050000
2015-09-15 20:32:15.345 OTGW: T00050000
2015-09-15 20:32:16.297 OTGW: Error 03
2015-09-15 20:32:17.227 OTGW: T00000300
2015-09-15 20:32:18.168 OTGW: T00000300
2015-09-15 20:32:19.121 OTGW: Error 03
2015-09-15 20:32:20.051 OTGW: T00000300
2015-09-15 20:32:20.140 OTGW: BC000030A
2015-09-15 20:32:20.605 OTGW: T00000300
2015-09-15 20:32:21.547 OTGW: T00000300
2015-09-15 20:32:21.636 OTGW: BC000030A
2015-09-15 20:32:22.101 OTGW: T00050000
2015-09-15 20:32:22.190 OTGW: BF0050000
2015-09-15 20:32:22.656 OTGW: T10013C00
2015-09-15 20:32:22.745 OTGW: BD0013C00
2015-09-15 20:32:23.211 OTGW: T10013C00
2015-09-15 20:32:23.300 OTGW: BD0013C00
2015-09-15 20:32:23.766 OTGW: T80190000
2015-09-15 20:32:23.855 OTGW: BC01924B3
2015-09-15 20:32:24.347 OTGW: T00110000
2015-09-15 20:32:24.436 OTGW: B40110F62
2015-09-15 20:32:24.902 OTGW: T801C0000
2015-09-15 20:32:24.991 OTGW: BC01C22B3
2015-09-15 20:32:25.457 OTGW: T801A0000
2015-09-15 20:32:25.546 OTGW: BC01A2C33
2015-09-15 20:32:26.011 OTGW: T00000300
2015-09-15 20:32:26.971 OTGW: T00000300
2015-09-15 20:32:27.060 OTGW: BC000030A
2015-09-15 20:32:27.526 OTGW: T001B0000
2015-09-15 20:32:27.615 OTGW: B601B0000
2015-09-15 20:32:28.080 OTGW: T10013C00
2015-09-15 20:32:29.032 OTGW: Error 03
2015-09-15 20:32:29.962 OTGW: T10013C00
2015-09-15 20:32:30.914 OTGW: Error 03
2015-09-15 20:32:31.845 OTGW: T00000300
2015-09-15 20:32:31.934 OTGW: BC000030A
2015-09-15 20:32:32.400 OTGW: T10013C00
2015-09-15 20:32:33.356 OTGW: Error 03
2015-09-15 20:32:34.287 OTGW: T10013C00
2015-09-15 20:32:35.239 OTGW: Error 03
2015-09-15 20:32:36.169 OTGW: T00000300
2015-09-15 20:32:37.254 OTGW: T00000300
2015-09-15 20:32:37.292 (Nefit) Lighting 2 (CH_enabled)
2015-09-15 20:32:37.295 (Nefit) Lighting 2 (CH_active)
2015-09-15 20:32:37.296 (Nefit) Lighting 2 (FlameOn)
2015-09-15 20:32:37.298 (Nefit) Temp (Control Setpoint)
2015-09-15 20:32:37.299 (Nefit) General/Percentage (Maximum Relative Modulation Level)
2015-09-15 20:32:37.300 (Nefit) Thermostat (Room Setpoint)
2015-09-15 20:32:37.301 (Nefit) General/Percentage (Relative modulation level)
2015-09-15 20:32:37.301 (Nefit) Temp (Room Temperature)
2015-09-15 20:32:37.302 (Nefit) Temp (Boiler Water Temperature)
2015-09-15 20:32:37.303 (Nefit) Temp (DHW Temperature)
2015-09-15 20:32:37.304 (Nefit) Temp (Outside Temperature)
2015-09-15 20:32:37.305 (Nefit) Temp (Return Water Temperature)
2015-09-15 20:32:37.306 (Nefit) Thermostat (DHW Setpoint)
2015-09-15 20:32:37.307 (Nefit) Thermostat (Max_CH Water Setpoint)
2015-09-15 20:32:39.003 OTGW: Error 03
2015-09-15 20:32:42.012 OTGW: Error 03
2015-09-15 20:32:48.241 OTGW: Error 03
2015-09-15 20:32:54.996 OTGW: Error 03
2015-09-15 20:32:56.897 OTGW: Error 03
2015-09-15 20:32:59.904 OTGW: Error 03
2015-09-15 20:33:08.731 OTGW: Error 03
2015-09-15 20:33:10.264 (Nefit) Lighting 2 (FlameOn)
2015-09-15 20:33:10.266 (Nefit) Temp (Control Setpoint)
2015-09-15 20:33:10.267 (Nefit) General/Percentage (Maximum Relative Modulation Level)
2015-09-15 20:33:10.268 (Nefit) Thermostat (Room Setpoint)
2015-09-15 20:33:10.269 (Nefit) General/Percentage (Relative modulation level)
2015-09-15 20:33:10.271 (Nefit) Temp (Room Temperature)
2015-09-15 20:33:10.273 (Nefit) Temp (Boiler Water Temperature)
2015-09-15 20:33:10.274 (Nefit) Temp (DHW Temperature)
2015-09-15 20:33:10.275 (Nefit) Temp (Outside Temperature)
2015-09-15 20:33:10.276 (Nefit) Temp (Return Water Temperature)
2015-09-15 20:33:10.278 (Nefit) Thermostat (DHW Setpoint)
2015-09-15 20:33:10.279 (Nefit) Thermostat (Max_CH Water Setpoint)
2015-09-15 20:33:20.051 OTGW: Error 02
2015-09-15 20:33:22.798 OTGW: Error 03
2015-09-15 20:33:24.681 OTGW: Error 03
2015-09-15 20:33:27.134 OTGW: Error 03
2015-09-15 20:33:29.016 OTGW: Error 03
2015-09-15 20:33:34.055 OTGW: Error 03
2015-09-15 20:33:42.485 (Nefit) Lighting 2 (FlameOn)
2015-09-15 20:33:42.487 (Nefit) Temp (Control Setpoint)
2015-09-15 20:33:42.488 (Nefit) General/Percentage (Maximum Relative Modulation Level)
2015-09-15 20:33:42.488 (Nefit) Thermostat (Room Setpoint)
2015-09-15 20:33:42.489 (Nefit) General/Percentage (Relative modulation level)
2015-09-15 20:33:42.490 (Nefit) General/Pressure (CH Water Pressure)
2015-09-15 20:33:42.491 (Nefit) Temp (Room Temperature)
2015-09-15 20:33:42.492 (Nefit) Temp (Boiler Water Temperature)
2015-09-15 20:33:42.494 (Nefit) Temp (DHW Temperature)
2015-09-15 20:33:42.495 (Nefit) Temp (Outside Temperature)
2015-09-15 20:33:42.496 (Nefit) Temp (Return Water Temperature)
2015-09-15 20:33:42.497 (Nefit) Thermostat (DHW Setpoint)
2015-09-15 20:33:42.498 (Nefit) Thermostat (Max_CH Water Setpoint)
2015-09-15 20:33:44.406 OTGW: Error 02
2015-09-15 20:33:54.299 OTGW: Error 03
2015-09-15 20:33:58.253 OTGW: Error 03
Between Errors most of the time the boiler, OTGW and thermostat are behaving normally. Any idea what causes this and what to do?
mfranken
Starting Member
Posts: 17 Joined: Mon Sep 07, 2015 10:29 am
Post
by mfranken » Tue Sep 15, 2015 8:45 pm
My setup, btw is:
my CV (Nefit TopLine Aquapower HRC 45/CW6 + EMS-OT)
Honeywell Touch modulation (TH8210M1003) thermostat
OpenTherm Gateway USB version bougth prebuilt, running latest firmware
Domoticz latest version on MacMIni
mfranken wrote: I have my setup running for a few days and it's not stable. I see a lot of Error 03, just like mentioned in this topic. I am using domoticz too. Today I saw T and B messages too:
Code: Select all
2015-09-15 20:29:53.953 OTGW: Error 03
2015-09-15 20:29:56.816 OTGW: Error 03
2015-09-15 20:30:01.689 OTGW: Error 03
2015-09-15 20:30:04.512 OTGW: Error 03
2015-09-15 20:30:07.355 OTGW: Error 03
2015-09-15 20:30:09.238 OTGW: Error 03
2015-09-15 20:30:14.132 OTGW: Error 03
2015-09-15 20:30:16.014 OTGW: Error 03
2015-09-15 20:30:17.896 OTGW: Error 03
2015-09-15 20:30:19.796 OTGW: Error 03
2015-09-15 20:30:20.301 (Nefit) Temp (Control Setpoint)
2015-09-15 20:30:20.302 (Nefit) General/Percentage (Maximum Relative Modulation Level)
2015-09-15 20:30:20.303 (Nefit) Thermostat (Room Setpoint)
2015-09-15 20:30:20.304 (Nefit) General/Percentage (Relative modulation level)
2015-09-15 20:30:20.305 (Nefit) Temp (Room Temperature)
2015-09-15 20:30:20.305 (Nefit) Temp (Boiler Water Temperature)
2015-09-15 20:30:20.306 (Nefit) Temp (DHW Temperature)
2015-09-15 20:30:20.307 (Nefit) Temp (Outside Temperature)
2015-09-15 20:30:20.308 (Nefit) Temp (Return Water Temperature)
2015-09-15 20:30:20.309 (Nefit) Thermostat (DHW Setpoint)
2015-09-15 20:30:20.309 (Nefit) Thermostat (Max_CH Water Setpoint)
2015-09-15 20:30:21.678 OTGW: Error 03
2015-09-15 20:30:23.560 OTGW: Error 03
2015-09-15 20:32:10.977 OTGW: T00000300
2015-09-15 20:32:11.940 OTGW: T00000300
2015-09-15 20:32:12.029 OTGW: B40000302
2015-09-15 20:32:12.495 OTGW: T00050000
2015-09-15 20:32:13.436 OTGW: T00050000
2015-09-15 20:32:14.377 OTGW: T00050000
2015-09-15 20:32:15.345 OTGW: T00050000
2015-09-15 20:32:16.297 OTGW: Error 03
2015-09-15 20:32:17.227 OTGW: T00000300
2015-09-15 20:32:18.168 OTGW: T00000300
2015-09-15 20:32:19.121 OTGW: Error 03
2015-09-15 20:32:20.051 OTGW: T00000300
2015-09-15 20:32:20.140 OTGW: BC000030A
2015-09-15 20:32:20.605 OTGW: T00000300
2015-09-15 20:32:21.547 OTGW: T00000300
2015-09-15 20:32:21.636 OTGW: BC000030A
2015-09-15 20:32:22.101 OTGW: T00050000
2015-09-15 20:32:22.190 OTGW: BF0050000
2015-09-15 20:32:22.656 OTGW: T10013C00
2015-09-15 20:32:22.745 OTGW: BD0013C00
2015-09-15 20:32:23.211 OTGW: T10013C00
2015-09-15 20:32:23.300 OTGW: BD0013C00
2015-09-15 20:32:23.766 OTGW: T80190000
2015-09-15 20:32:23.855 OTGW: BC01924B3
2015-09-15 20:32:24.347 OTGW: T00110000
2015-09-15 20:32:24.436 OTGW: B40110F62
2015-09-15 20:32:24.902 OTGW: T801C0000
2015-09-15 20:32:24.991 OTGW: BC01C22B3
2015-09-15 20:32:25.457 OTGW: T801A0000
2015-09-15 20:32:25.546 OTGW: BC01A2C33
2015-09-15 20:32:26.011 OTGW: T00000300
2015-09-15 20:32:26.971 OTGW: T00000300
2015-09-15 20:32:27.060 OTGW: BC000030A
2015-09-15 20:32:27.526 OTGW: T001B0000
2015-09-15 20:32:27.615 OTGW: B601B0000
2015-09-15 20:32:28.080 OTGW: T10013C00
2015-09-15 20:32:29.032 OTGW: Error 03
2015-09-15 20:32:29.962 OTGW: T10013C00
2015-09-15 20:32:30.914 OTGW: Error 03
2015-09-15 20:32:31.845 OTGW: T00000300
2015-09-15 20:32:31.934 OTGW: BC000030A
2015-09-15 20:32:32.400 OTGW: T10013C00
2015-09-15 20:32:33.356 OTGW: Error 03
2015-09-15 20:32:34.287 OTGW: T10013C00
2015-09-15 20:32:35.239 OTGW: Error 03
2015-09-15 20:32:36.169 OTGW: T00000300
2015-09-15 20:32:37.254 OTGW: T00000300
2015-09-15 20:32:37.292 (Nefit) Lighting 2 (CH_enabled)
2015-09-15 20:32:37.295 (Nefit) Lighting 2 (CH_active)
2015-09-15 20:32:37.296 (Nefit) Lighting 2 (FlameOn)
2015-09-15 20:32:37.298 (Nefit) Temp (Control Setpoint)
2015-09-15 20:32:37.299 (Nefit) General/Percentage (Maximum Relative Modulation Level)
2015-09-15 20:32:37.300 (Nefit) Thermostat (Room Setpoint)
2015-09-15 20:32:37.301 (Nefit) General/Percentage (Relative modulation level)
2015-09-15 20:32:37.301 (Nefit) Temp (Room Temperature)
2015-09-15 20:32:37.302 (Nefit) Temp (Boiler Water Temperature)
2015-09-15 20:32:37.303 (Nefit) Temp (DHW Temperature)
2015-09-15 20:32:37.304 (Nefit) Temp (Outside Temperature)
2015-09-15 20:32:37.305 (Nefit) Temp (Return Water Temperature)
2015-09-15 20:32:37.306 (Nefit) Thermostat (DHW Setpoint)
2015-09-15 20:32:37.307 (Nefit) Thermostat (Max_CH Water Setpoint)
2015-09-15 20:32:39.003 OTGW: Error 03
2015-09-15 20:32:42.012 OTGW: Error 03
2015-09-15 20:32:48.241 OTGW: Error 03
2015-09-15 20:32:54.996 OTGW: Error 03
2015-09-15 20:32:56.897 OTGW: Error 03
2015-09-15 20:32:59.904 OTGW: Error 03
2015-09-15 20:33:08.731 OTGW: Error 03
2015-09-15 20:33:10.264 (Nefit) Lighting 2 (FlameOn)
2015-09-15 20:33:10.266 (Nefit) Temp (Control Setpoint)
2015-09-15 20:33:10.267 (Nefit) General/Percentage (Maximum Relative Modulation Level)
2015-09-15 20:33:10.268 (Nefit) Thermostat (Room Setpoint)
2015-09-15 20:33:10.269 (Nefit) General/Percentage (Relative modulation level)
2015-09-15 20:33:10.271 (Nefit) Temp (Room Temperature)
2015-09-15 20:33:10.273 (Nefit) Temp (Boiler Water Temperature)
2015-09-15 20:33:10.274 (Nefit) Temp (DHW Temperature)
2015-09-15 20:33:10.275 (Nefit) Temp (Outside Temperature)
2015-09-15 20:33:10.276 (Nefit) Temp (Return Water Temperature)
2015-09-15 20:33:10.278 (Nefit) Thermostat (DHW Setpoint)
2015-09-15 20:33:10.279 (Nefit) Thermostat (Max_CH Water Setpoint)
2015-09-15 20:33:20.051 OTGW: Error 02
2015-09-15 20:33:22.798 OTGW: Error 03
2015-09-15 20:33:24.681 OTGW: Error 03
2015-09-15 20:33:27.134 OTGW: Error 03
2015-09-15 20:33:29.016 OTGW: Error 03
2015-09-15 20:33:34.055 OTGW: Error 03
2015-09-15 20:33:42.485 (Nefit) Lighting 2 (FlameOn)
2015-09-15 20:33:42.487 (Nefit) Temp (Control Setpoint)
2015-09-15 20:33:42.488 (Nefit) General/Percentage (Maximum Relative Modulation Level)
2015-09-15 20:33:42.488 (Nefit) Thermostat (Room Setpoint)
2015-09-15 20:33:42.489 (Nefit) General/Percentage (Relative modulation level)
2015-09-15 20:33:42.490 (Nefit) General/Pressure (CH Water Pressure)
2015-09-15 20:33:42.491 (Nefit) Temp (Room Temperature)
2015-09-15 20:33:42.492 (Nefit) Temp (Boiler Water Temperature)
2015-09-15 20:33:42.494 (Nefit) Temp (DHW Temperature)
2015-09-15 20:33:42.495 (Nefit) Temp (Outside Temperature)
2015-09-15 20:33:42.496 (Nefit) Temp (Return Water Temperature)
2015-09-15 20:33:42.497 (Nefit) Thermostat (DHW Setpoint)
2015-09-15 20:33:42.498 (Nefit) Thermostat (Max_CH Water Setpoint)
2015-09-15 20:33:44.406 OTGW: Error 02
2015-09-15 20:33:54.299 OTGW: Error 03
2015-09-15 20:33:58.253 OTGW: Error 03
Between Errors most of the time the boiler, OTGW and thermostat are behaving normally. Any idea what causes this and what to do?
mfranken
Starting Member
Posts: 17 Joined: Mon Sep 07, 2015 10:29 am
Post
by mfranken » Tue Sep 15, 2015 9:04 pm
Answering my own question for archaeologists sake: I read the troubleshooting guide and attached the OTGW to the otmonitor, set VR=4 and the Errors are gone (for now)
hvxl
Senior Member
Posts: 2029 Joined: Sat Jun 05, 2010 11:59 am
Contact:
Post
by hvxl » Tue Sep 15, 2015 9:46 pm
That was also the suggestion offered to the previous poster in this topic...
By the way: Is Domoticz hiding information? With the latest firmware the OTGW should report additional information after Error 02, which I don't see in your log.
Schelte
mfranken
Starting Member
Posts: 17 Joined: Mon Sep 07, 2015 10:29 am
Post
by mfranken » Tue Sep 15, 2015 10:38 pm
Thanks, I will check the domoticz implementation